What does M6 to M20 threaded rod carry?
The table gives the allowable tensile force in the steel at a safety factor of 2. Stress areas come from ISO 898-1; yield strength is 0.8 × nominal tensile strength (320 N/mm² for 4.8 and 640 N/mm² for 8.8).
| Size | 4.8 (kN) | 4.8 (kg) | 8.8 (kN) | 8.8 (kg) |
|---|---|---|---|---|
| M6 | 3.22 | 328 | 6.43 | 656 |
| M8 | 5.86 | 597 | 11.71 | 1,194 |
| M10 | 9.28 | 946 | 18.56 | 1,892 |
| M12 | 13.49 | 1,375 | 26.98 | 2,750 |
| M16 | 25.12 | 2,561 | 50.24 | 5,121 |
| M20 | 39.20 | 3,996 | 78.40 | 7,992 |
Stress area: ISO 898-1 (standard value). Calculation: own formula, indicative.
What else should you check?
- The anchor in the soffit: its permitted load is given by the manufacturer and is often lower than the rod's
- The nut and the channel nut in the channel
- The soffit itself: concrete, steel or timber
- Fire: circuit integrity requires much lower stresses, per the manufacturer's tables
- Dynamic loads and vibration
Frequently asked questions
How much load can M10 threaded rod take?
In grade 4.8 with a safety factor of 2, the allowable tensile force in the steel is about 9.3 kN (around 946 kg). Grade 8.8 doubles that. The anchor, nut and soffit often set a lower limit. Indicative; the manufacturer confirms.
How much weight can threaded rod hold?
That depends on size, property class and safety factor. In grade 4.8 with factor 2: M6 about 328 kg, M8 about 597 kg, M10 about 946 kg, M12 about 1,375 kg. Always check the fixing to the soffit.
How do you fix threaded rod into concrete?
With a ceiling anchor (for example a drop-in or wedge anchor) rated for the load and for cracked or uncracked concrete. The anchor's permitted load is in the manufacturer's documentation and is often lower than the rod's.
What do 4.8 and 8.8 mean?
The property class. The first number × 100 is the tensile strength in N/mm² (400 or 800); the second gives the yield-to-tensile ratio (0.8). Grade 8.8 is therefore twice as strong as 4.8.